I am new to this forum (thanks bbb) and have a problem with my lights... I have 6 500 watt halogen lights and just bought a 3500 watt powertrain generator and it will only run 4 of the 6 lights. I thought the cord was the problem so I split it up the light on 2 separate plugs and it still only runs 4. I do not know enough about this topic to fix my problem obviously so maybe one of yall can help me.

Thanks in advance for any help.
Ben
Post #157629
Posted 8/5/2008 1:52:01 PM
Sailfish

SailfishSailfishSailfishSailfishSailfishSailfishSailfishSailfish

Group: Forum Members
Last Login: Today @ 1:27:14 PM
Posts: 1,972, Visits: 10,970
sounds to me to much wattage for the generator,but im sure the others on here will have a better idea.....

Post #157631
Posted 8/5/2008 1:56:47 PM


Mingo

MingoMingoMingoMingoMingoMingoMingoMingo

Group: Forum Members
Last Login: 6/29/2009 3:50:55 PM
Posts: 62, Visits: 104
Your generator is 3500 starting watts but how many running watts?

Your lights need 3000 watts to run but probably more to start up.

Also sometimes you need to look at amps and see how many amps your pulling and how many amps your generator puts out.

Sounds like you're just overloading the generator.

Honda EU2000i generator running 6 HPS 150 watt lights on a 18ft Dixon aluminum boat with a 31 godevil. Powered in the shallows by a 55# thrust Minn Kota.

Post #157639
Posted 8/5/2008 2:06:23 PM


White Marlin

White MarlinWhite MarlinWhite MarlinWhite MarlinWhite MarlinWhite MarlinWhite MarlinWhite Marlin

Group: Forum Members
Last Login: 7/1/2009 9:56:16 AM
Posts: 3,369, Visits: 12,419
bbb (8/5/2008)
Your generator is 3500 starting watts but how many running watts?

Your lights need 3000 watts to run but probably more to start up.

Also sometimes you need to look at amps and see how many amps your pulling and how many amps your generator puts out.

Sounds like you're just overloading the generator.

If he has a powertrain 3500, it is rated for 3500 continuous with 4450 starting.

PT-3500 ELECTRIC START GENERATOR - POWERTRAIN
$590.00
PowerTrain 3500W 6.5hp Generator - Electric Start
Features:
• 2 120 volt plug ins
• 1 240 volt twist lock plug 20 amp
• 1 120 volt twist lock plug 30 amp
• 10 amp battery charger
• Gel sealed battery
• Volt meter
• Twist lock plugs
• 10" pneumatic wheel kit with fold away handles
• 1 year limited warranty
• 1.5" Diameter steel frame
• Emissions compliant in all states except CA
Specifications:

Continuous Output  3500 watts  
Maximum output  4450 watts  

Now most likely you are over burdening the outlet output rating of 20 amps.  Most small generators will not give you more than 20 amps out of a normal 3 prong 120V outlet.  I see that your generator has 1 120 volt twist lock plug that is 30 amps.  You might need to create a juntion box with normal 3 prong outlets to plug your lights into from this 30 amp outlet.

But at 500 watts and 110-120 volts each light is drawing about 4.5 amps for a total parallel draw of 27 amps for all 6 lights.  Which exceeds the 20 amp rating for the 2 120 volt plug ins on your generator.

-------------------------------------------------------------------------------------------------------------

 

"H2O:  2 parts hydrogen 1 part obsession."

 

 

Jon


 

Post #157643
Posted 8/5/2008 2:08:21 PM


Grouper

GrouperGrouperGrouperGrouperGrouperGrouperGrouperGrouper

Group: Forum Members
Last Login: 2 days ago @ 11:56:55 PM
Posts: 809, Visits: 1,990
whitebc13 (8/5/2008)
I am new to this forum (thanks bbb) and have a problem with my lights... I have 6 500 watt halogen lights and just bought a 3500 watt powertrain generator and it will only run 4 of the 6 lights. I thought the cord was the problem so I split it up the light on 2 separate plugs and it still only runs 4. I do not know enough about this topic to fix my problem obviously so maybe one of yall can help me.

Thanks in advance for any help.
Ben

Your generator is most likely only designed to only put out between 2800-3000 watts continuously and 3500 in a surge as when you are starting up something that has a heavy draw to start with and then evens out.  My Honda 2000 is only rated to continuously put out 1600 watts.  If this isn't the case your probably still gonna be having problems with to much amp draw.  Is the circuit breaker tripping?  I need a little more info to properly address the question.

"SHARP GIGS AND TIGHT RIGS"

Post #157644
Posted 8/5/2008 2:41:26 PM
Ruby Red Lip

Ruby Red LipRuby Red LipRuby Red LipRuby Red LipRuby Red LipRuby Red LipRuby Red LipRuby Red Lip

Group: Forum Members
Last Login: 2/2/2009 10:43:00 AM
Posts: 30, Visits: 147
Telum Piscis (8/5/2008)
bbb (8/5/2008)
Your generator is 3500starting watts but how many running watts?

Your lights need 3000 watts to run butprobably more to start up.

Also sometimes you need to look at amps and see how many amps your pulling and how many amps your generator puts out.

Sounds like you're just overloading the generator.


If he has a powertrain 3500, it is rated for 3500 continuous with 4450 starting.

PT-3500 ELECTRIC START GENERATOR - POWERTRAIN
$590.00
PowerTrain 3500W 6.5hp Generator - Electric Start
Features:
• 2 120 volt plug ins
• 1 240 volt twist lock plug 20 amp
• 1 120 volt twist lock plug 30 amp
• 10 amp battery charger
• Gel sealed battery
• Volt meter
• Twist lock plugs
• 10" pneumatic wheel kit with fold away handles
• 1 year limited warranty
• 1.5" Diameter steel frame
• Emissions compliant in all states except CA
Specifications:

Continuous Output 3500 watts
Maximum output 4450 watts


Now most likely you are over burdening the outlet output rating of 20 amps. Most small generators will not give you more than 20 amps out of a normal 3 prong120V outlet. I see that your generator has 1 120 volt twist lock plug that is 30 amps. You might need to create a juntion box with normal 3 prong outlets to plug your lights into from this 30 amp outlet.

But at 500 watts and 110-120 volts each light is drawing about 4.5 amps for a total parallel draw of 27 amps for all 6 lights. Which exceeds the 20 amp rating for the2 120 volt plug ins on your generator.



that is the generator that I have I will try the hook up like you are talking about tonight and let yall know how it works tomm. thanks!
Post #157656
Posted 8/5/2008 4:24:10 PM


Mingo

MingoMingoMingoMingoMingoMingoMingoMingo

Group: Forum Members
Last Login: 5/5/2009 7:42:06 PM
Posts: 87, Visits: 1,054
What size wire do you have going to the lights? Is is a standard 14 or 16 gauge extension cord? Your best option would be to buy 300 watt bulbs and change them out. Not much difference in light output and would cut your amps down to around 15 amps, which your generator will handle. Also, measure the voltage on one of the plugs with the lights on and see if the generator is putting out 120 volts with that kind of load on it. If the voltage drops, the amps go up.

Post #157693
Posted 8/5/2008 4:47:43 PM
Ruby Red Lip

Ruby Red LipRuby Red LipRuby Red LipRuby Red LipRuby Red LipRuby Red LipRuby Red LipRuby Red Lip

Group: Forum Members
Last Login: 2/2/2009 10:43:00 AM
Posts: 30, Visits: 147
The circuit breaker is throwing when I turn on light number 5, after about 30 sec of motor struggling, and as soon as I hit the switch for number 6...

I think that it is a 12 or 14 gauge ext cord.. The package said HEAVY DUTY but you know how that works...
Post #157709
Posted 8/5/2008 9:03:15 PM


Grouper

GrouperGrouperGrouperGrouperGrouperGrouperGrouperGrouper

Group: Forum Members
Last Login: 2 days ago @ 11:56:55 PM
Posts: 809, Visits: 1,990
I used 300s when I had halos and didn't see much difference in light output between them and 500s either.  I have heard some guys talking about using the 350 Ultras. They are supposed to put out more light than the 500s.  I think that Sylvania makes them But I am not sure, if someone else knows some more maybe they can add to this.

"SHARP GIGS AND TIGHT RIGS"
Post #157878
Posted 8/5/2008 9:17:31 PM


Mingo

MingoMingoMingoMingoMingoMingoMingoMingo

Group: Forum Members
Last Login: 6/29/2009 3:50:55 PM
Posts: 62, Visits: 104
I agree with these guys.  Go to HD or Lowes and get some 300 watt bulbs.

With my 2nd setup, I bought 4 of the 500 watt halogens and changed the bulbs out to 300 watt.  Still a bunch of light with 300 watts.  Its the easiest and least expensive thing you can do to solve the problem.

Honda EU2000i generator running 6 HPS 150 watt lights on a 18ft Dixon aluminum boat with a 31 godevil. Powered in the shallows by a 55# thrust Minn Kota.

Post #157889
Posted 8/5/2008 9:18:18 PM


Snapper

SnapperSnapperSnapperSnapperSnapperSnapperSnapperSnapper

Group: Forum Members
Last Login: Yesterday @ 8:50:36 PM
Posts: 412, Visits: 1,517
Go with # 10 wire and try to stagger the lights when you turn them on. Turn on 3 first and then add one maybe two after the first three are heated up. I know this sounds like a pain but this may be what you need to do if you want to run that set up. I would agree with the above post if you don't want to do it this way you could try using 300 watt instead of the 500.

Richard

16' Wellcraft (Tammy II)

 Wise men talk because they have something to say. Fools talk because they have to say something.

Plato
Post #157890
Posted 8/6/2008 2:28:26 AM


Snapper

SnapperSnapperSnapperSnapperSnapperSnapperSnapperSnapper

Group: Forum Members
Last Login: Yesterday @ 11:06:22 PM
Posts: 328, Visits: 1,549
I may be wrong, but I don't think there is an amp drop on those lights after start up (like the hps lights). It is going to be your amp draw kicking the breaker out. Buy the correct size SO cord for amps drawn and a 30 amp twist lock plug and it should fix your problem.

Here is a link for you:http://www.elec-toolbox.com/calculators/voltdrop.htm

Post #157971
« Prev Topic | Next Topic »


All times are GMT -6:00, Time now is 1:49pm

   Pensacola Fishing Fourm


This site is also available at:
http://www.fishinginflorida.info  http://www.fishinginalabama.info http://www.destinfishingforum.com
http://www.orangebeachfishingforum.com
  http://www.fishthebridge.com   http://www.pensacolahuntingforum.com  http://www.pensacoladivingforum.com